The max amps is 24amps as it is a 30amp pdu. The 20amp is in reference to pdu port meaning it has a max of 20amps on a port. So running two ports at 10amps is perfectly safe.
Ok thank you! So it seems that the pdus will have a lot of wasted plugs if you plug in the s19s since one will pull 20A and the max for the PDU is 24A.
Are there any alternatives or would this be the best course of action for Bitcoin mining?
at 3250W will be 13.5amps using 240v so on a 30amp pdu you can run 2 s19’s. PDU’s are designed for servers and running multiple desktops hence why they have alot of plugs
Ok cool! Thank you, and just making sure, it would be one S19 per pdu, so if I want to have 10 S19s, I would need 10 PDUs.
If I was planning on scaling up to that number or more, would it be more cost effective to look at a different option such as having it hard wired by an electrician or is this just the better option since it has the surge protection along with it?
Safely you can only run 1 on each pdu… always follow the 80% rule… 30amp pdu should only run 24amp of constant power max.
Miners are 13.5amps each. So 2x is 27amps. I personally wouldn’t do that if I were you
What you need to do is get real word data for each miner run each one and see what your amps watts etc are. All data i used was from bitmain so those numbers could be high or lower. You may be able to lower the frequency to a point where you can run 2 att the 80% on one PDU.